Neat! Does the fan ever run Mike?
Mike-How much did that bad boy cost?
when you consider the cost of many stand alone conditioners, and depending on the layout of your system you may have several conditioners, the Equi=tech is a no-brainer for a serious system. it may not work for everyone dealing with existing situations and amperage availabilities. but if you have space and an extra 50-70 amps to spare from your service it makes lots of sense.
This is an interesting post. Since external grounding is required, what's considered 'best practice' for audio purposes?Ground Rod Safety
Ground rods are only about safety during thunder & lighting storms! Ground rods do not improve audio quality and sometimes diminish it. Power line noise, leakage and interference currents do not flow through the ground rod into Mother Earth and disappear. Power line noise, leakage currents will take all possible paths to return to their sources, if much of this current flows back to the source through the ground rod then your power wiring system has a big problem.
The electrical code and the safety of both humans and your equipment require that all ground rods be bonded together outside the building and only be connected to your power system at the building service entrance.
You just have to live with the requirement.
Everything that you need to know about AC power wiring and Audio/Video system is in these papers:
The importance of the ground system to the audio system is from the service entrance / main breaker box (panel-board) and inward inside your building. From the service entrance outward to the ground rod is about thunder storms.
The Bill Whitlock of Jensen Transformers Seminar paper
http://www.jensen-transformers.com/an/generic seminar.pdf
The Jim Brown of Audio Systems Group white paper
"Power and Grounding for Audio and Audio/Video Systems"
http://www.audiosystemsgroup.com/SurgeXPowerGround.pdf
"Power White Paper" from Middle Atlantic.com
http://www.middleatlantic.com/power.htm
or a different version of the same paper
"The TRUTH" from ExactPower of Middle Atlantic Products
http://www.exactpower.com/elite/wpapers.aspx
(hope all the links still work)
Bill Whitlock wrote this 12 years ago.
GROUND RODS: magic noise sinks?
http://svconline.com/mag/avinstall_ground_rods_magic/
Speedskater; many thanks for the enlightenment.
since i'm in a separate building quite a ways away from the ground for my main service does that affect the thinking about a separate ground?
Yes, a detached building requires it's own ground rods.
Thoughts on ground rods - from the Jim Brown paper:
Following the guidelines below is generally
enough to satisfy the needs of audio and video system earthing. Also, the earth electrode
system will be in parallel with building steel and the concrete foundation. In general,
the impedance to earth of the earth electrode system will be minimized by:
1. Using more earth electrodes.
2. Making the earth electrodes longer, driving them deeper into the earth. Ten feet
(3 meters) is generally considered to be a minimum depth.
3. Spacing earth electrodes as far apart as practical (spacing equal to at least their
length). Separation is important because mutual coupling between closely
spaced electrodes increases their impedance to earth.
4. Placing electrodes where they will be continuously exposed to moisture (rainfall).
For this reason, earth electrodes should be outside the building footprint.
5. Avoiding chemically enhanced electrode systems. These systems require long
term attention to maintain their chemical balance. Few facilities are likely to
have staff trained to do this.
6. Increasing the surface area in contact with the earth, or by using an electrode of
greater cross-section of greater length, or by means of a Ufer (an earth electrode
buried in concrete). (Fig 12)
One thing to watch out for is interconnects and other signal wires running from building to building. They need ground blocks at the build entrance. A nearby lightning surge can develop thousands of volts between buildings.
Thank you Speedskater. Very helpful. My next build-out won't be for some months, but I'm pulling together all the info I can. I haven't found a property to buy in our new location yet, but we'll get there. If you are ever in Austin, once I'm fully set up, you have a standing invitation.Yes, a detached building requires it's own ground rods.